1394 Posts Member #: 1346 Post Whore bromsgrove |
8th May, 2013 at 08:15:26pm
I have a ariston class he 30 boiler approx. 18months old. The pressure on the boiler keeps going up, today it has been 3.5 bar. I have released water from a radiator to bring the pressure back down but it comes back up. I have turned off both taps that fill up the tank, but it still goes up. The vessel does not have a valve to put any air back in. I have drained the system today, but to no avail. Any advice would be great. Thanks |
||||||
![]() 1043 Posts Member #: 10424 Post Whore Swansea boyo! |
8th May, 2013 at 08:18:56pm
Sounds like your vessel has gone :( They don't die, they just get faster! |
||||||
![]() 1043 Posts Member #: 10424 Post Whore Swansea boyo! |
8th May, 2013 at 08:20:45pm
I'm surprised that your vessel doesn't have a point to recharge (you could have used a tyre pressure gauge to see how much air, if any was in there. If water came straight out you would know straight away that the vessel had pin holed) it but a lot of them do lose the air/pin hole. Does the pressure just build when the boiler is on then drop when it switches off/gets cold? If so I'd say it's most likely the vessel which isn't really too hard to change (dump the water in the boiler, take it out, put the new one in then fill him back up Edited by Shauna on 8th May, 2013. They don't die, they just get faster! |
||||||
![]() 9812 Posts Member #: 332 Resident Cylinder Head Modifier Mitsi Evo 7, 911, Cossie. & all the chavs ...... won no problem |
8th May, 2013 at 09:25:54pm
passing fill valve when shut, and or both of them passing slightly creaping the pressure up check them out or replace them, there are a lot of hung wang ball valves on the market.
|
||||||
![]() 1755 Posts Member #: 8852 Post Whore leicestershire |
8th May, 2013 at 10:20:04pm
Could be the plate heat exchanger. If it bursts between heating and water then it will pressurize the heating. Turn a hot tap on and see what the gauge does.
13.95 1/4 mile on a 2.95 fd. Carnt be that hard to beat! |
||||||
|
1394 Posts Member #: 1346 Post Whore bromsgrove |
9th May, 2013 at 05:04:59am
I also thought the vessel, but can I find it no!! it has completely disappeared if it was ever there before.
|
||||||
![]() 1043 Posts Member #: 10424 Post Whore Swansea boyo! |
9th May, 2013 at 06:09:50am
You can't find the vessel? If it is one of those round ones I'd guess it's hidden behind everything at the back.
They don't die, they just get faster! |
||||||
|
1394 Posts Member #: 1346 Post Whore bromsgrove |
9th May, 2013 at 06:38:05am
On 9th May, 2013 ShaunaFTW said:
You can't find the vessel? If it is one of those round ones I'd guess it's hidden behind everything at the back. If the plate had pin holed inside (I've never seen this but I guess it's possible) surely his hot water would be coming out all mucky because they were mixing? I can't see the vessel to put the pressure up unless it is enclosed in another unit. I am going to turn the water off over night and see what happens, the pressure was 3.5 bar this morning. That way I can rule out whether it is a valve or not. But I suspect I will have to get an engineer out. |
||||||
![]() 1043 Posts Member #: 10424 Post Whore Swansea boyo! |
9th May, 2013 at 06:55:44am
The way to tell if it's the vessel is to run the boiler (I do it at max) if the pressure rises as it's getting hotter and then eventually blows off its the vessel because it's not compensating for the heat (hence the name expansion vessel They don't die, they just get faster! |
||||||
|
1394 Posts Member #: 1346 Post Whore bromsgrove |
9th May, 2013 at 07:14:18am
It is rising when the boiler is not running, so yes I agree it is more likely to be the vessel, But I can't see the vessel unless it is enclosed in the black unit within the pics below. Filling loop is always off. My boiler is only 18months-2years old and I have to say we have had no probs until now.
On 9th May, 2013 ShaunaFTW said:
The way to tell if it's the vessel is to run the boiler (I do it at max) if the pressure rises as it's getting hotter and then eventually blows off its the vessel because it's not compensating for the heat (hence the name expansion vessel ). If it's not rising when the boiler is off then it's likely to be the vessel. Your filling loop should always be off other than to add more water (pressure) into the system so if it's rising when cold then it will be the valves passing.
Aniston aren't great though from what I know (I deal with ones that are 10years old and more often than not we rip them out and put in a baxi/vaillant) |
||||||
![]() 16540 Posts Member #: 4241 King Gaycharger, butt plug dealer, Sheldon Cooper and a BAC but generally a niceish fella if you dont mind a northerner Rotherham, South Yorkshire |
9th May, 2013 at 07:16:11am
If it's under warranty still, call them out. Don't waste your time trying to sort it yourself as you risk invalidating your warranty. On 11th Feb, 2015 robert said:
i tried putting soap on it , and heating it to brown , then slathered my new lube on it
|
||||||
![]() 1755 Posts Member #: 8852 Post Whore leicestershire |
9th May, 2013 at 07:46:03am
Thats the heat exchanger. The vessal will be down the back.
13.95 1/4 mile on a 2.95 fd. Carnt be that hard to beat! |
||||||
|
336 Posts Member #: 9941 Senior Member Derby |
9th May, 2013 at 09:45:32pm
as said above if its rising in pressure when its turned off its going to be the heat exchanger, call the manufacturer if its still under warrantee! |
||||||
|
1394 Posts Member #: 1346 Post Whore bromsgrove |
10th May, 2013 at 04:20:25am
thanks, will be calling them today, have turned off the water at the mains and no rise over night. |
||||||
| Home > General Chat > OT need help with combi boiler pressure | |||||||
|
|||||||
| Page: |


) Or you could just put an external vessel on somewhere in the system.