The 40A / 30ma RCCD in my workshop keeps tripping when my milling machine is on, no doubt the 30 year old motors have some small earth leakage. How can I get around this problem? How dodgy is it to replace the RCCD with 100ma or just a normal over current breaker? On 15th May, 2009 TurboDave said:
I think the welsh one has it right! 1st to provide running proof of turbo twinkie in a car and first to run a 1/4 in one!! Is your data backed up?? one extra month free for all Turbo minis members, PM me for detials |
||||||
![]() 3673 Posts Member #: 9300 Post Whore Quarry Bonk |
29th Nov, 2013 at 04:10:27am
If it were me and You have the space, I'd come off the incoming side from the main board, and put a separate small board in (just a 2 gang) and put a normal rcb in it to the current rating of the mill, making it it's own dedicated supply. On 26th Jan, 2012 Tom Fenton said:
ring problems are down to wear or abuse but although annoying it isn't a show stopper On 5th Aug, 2014 madmk1 said:
Shit the bed! I had snapped the end of my shaft off!! 17.213 @ 71mph, 64bhp n/a (Old Engine) |
||||||
![]() 1425 Posts Member #: 9199 Post Whore Lancashire |
29th Nov, 2013 at 08:01:52am
They say it only takes 50mA to kill you, thats why most consumer units are fitted with the 30mA RCCD.
What the mind can conceive the mini can achieve
|
||||||
![]() 11046 Posts Member #: 965 Post Whore Preston On The Brook |
29th Nov, 2013 at 08:13:11am
On 29th Nov, 2013 lee.pb said:
They say it only takes 50mA to kill you, thats why most consumer units are fitted with the 30mA RCCD. Its up to you if you want to up it. My company say that the 30ma can still kill you and is why they issue us all with 10ma RCD's. When I pointed out they were made in China, I got that face of realisation from the EH&S manager
On 26th Oct, 2004 TurboDave16v said:
Is it A-Series only? I think it should be... So when some joey comes on here about how his 16v turbo vauxhall is great compared to ours, he can be given the 'bird'... On 26th Oct, 2004 Tom Fenton said:
Yep I agree with TD........ |
||||||
![]() 11046 Posts Member #: 965 Post Whore Preston On The Brook |
29th Nov, 2013 at 08:18:02am
Jim, you are using a phase inverter, the motor s on the mill are not directly coupled to the mains supply are they?
On 26th Oct, 2004 TurboDave16v said:
Is it A-Series only? I think it should be... So when some joey comes on here about how his 16v turbo vauxhall is great compared to ours, he can be given the 'bird'... On 26th Oct, 2004 Tom Fenton said:
Yep I agree with TD........ |
||||||
![]() 6752 Posts Member #: 828 Post Whore uranus |
29th Nov, 2013 at 08:49:31am
i had the same problem with the flowbench motor jim . I was using a vfd, and apparently these shoot a bit of dc down the return which reads as an imbalance on the rcb and trips it .
Medusa + injection = too much torque for the dyno ..https://youtu.be/qg5o0_tJxYM |
||||||
![]() 2406 Posts Member #: 341 aka T2clubby South Staffs |
29th Nov, 2013 at 01:10:10pm
As Robert says, run a dedicated non RCD supply just for that machine and make sure it has a good earth. Just don't get looping any sockets off it for anything else! |
||||||
|
Site Admin ![]() 9407 Posts Member #: 58 455bhp per ton 12 sec 1/4 mile road legal mini Sunny Bridgend, South Wales |
29th Nov, 2013 at 01:50:20pm
I'll do as Robert suggests, I'm using a rotary phase converter and a VFD so that would explain the issues.
On 15th May, 2009 TurboDave said:
I think the welsh one has it right! 1st to provide running proof of turbo twinkie in a car and first to run a 1/4 in one!! Is your data backed up?? one extra month free for all Turbo minis members, PM me for detials |
||||||
|
Site Admin ![]() 9407 Posts Member #: 58 455bhp per ton 12 sec 1/4 mile road legal mini Sunny Bridgend, South Wales |
29th Nov, 2013 at 06:28:10pm
This is getting more odd. Coming out of my mains supply meter I have two pairs of 16mm2 cable. One set goes to my house consumer unit, and the other out to my workshop.
On 15th May, 2009 TurboDave said:
I think the welsh one has it right! 1st to provide running proof of turbo twinkie in a car and first to run a 1/4 in one!! Is your data backed up?? one extra month free for all Turbo minis members, PM me for detials |
||||||
|
4018 Posts Member #: 1757 Back to Fucking Tool status Swindon |
29th Nov, 2013 at 06:38:45pm
Having covered it in first aid and electronics and EEP 30ma can kill you, as low as 26ma has been known to stop a heart of an unhealthy person Drives
|
||||||
|
Site Admin ![]() 9407 Posts Member #: 58 455bhp per ton 12 sec 1/4 mile road legal mini Sunny Bridgend, South Wales |
29th Nov, 2013 at 07:32:47pm
Any ideas how I can work out where in the machine the fault is? With the main spindle
On 15th May, 2009 TurboDave said:
I think the welsh one has it right! 1st to provide running proof of turbo twinkie in a car and first to run a 1/4 in one!! Is your data backed up?? one extra month free for all Turbo minis members, PM me for detials |
||||||
|
1713 Posts Member #: 8480 MS Paint flat cap champion & Morris Ital Lover From Sheffield now live in York tha noz |
29th Nov, 2013 at 11:06:28pm
Its all very well taking rcd's out of the way for one circuit blah blah ect ect-but to comply with the regs its only ok if the earth fault loop impedance(Zs)for that circuit is low enough-or if your on a TT system a) the zs will more than certainly be too high and b)there will most likely be one big rccd protecting the main incomer-if this is the case either way, to keep it safe and in the regs your fucked.
Edited by oli79 on 29th Nov, 2013. On 18th Oct, 2013 apbellamy said:
I am feeling particularly BACish today. On 5th Oct, 2014 Shauna said:
What that's crazy, you go commando hahaha! How heavy is your helmet ? The Morris Ital assassin! |
||||||
|
3594 Posts Member #: 655 Post Whore Northern Ireland |
29th Nov, 2013 at 11:32:57pm
On 29th Nov, 2013 Jimster said:
Any ideas how I can work out where in the machine the fault is? With the main spindle motor not running I still get same issue. You said it's now connected to source with no RCD's in place though, but it is now tripping an RCD elsewhere, on a totally different board ? That sounds like there could be a neutral or something linked between two boards ( ie outgoing circuits ) which is screwing things up when you turn something on. So when you turn power on, some current goes out via another path and not through the intended RCD It may be a fault with the machine or it's controls. You could try disconnecting/isolating say the motor, the controls and powering the unit up to see when it trips. Is this a new circuit wired in for the machine ? Or stuff added on to service it ? As above, pics of any boards and what's going on might help 9.85 @ 145mph
|
||||||
|
1713 Posts Member #: 8480 MS Paint flat cap champion & Morris Ital Lover From Sheffield now live in York tha noz |
30th Nov, 2013 at 12:16:18am
If indeed there was a link/cross between the two rcds then they would trip as soon any meaning full load was pulled from any circuit connected to them- ie more than 30 ma,in reality if that condition existed you would most likely have a job on even getting the rcd to stay in.
On 18th Oct, 2013 apbellamy said:
I am feeling particularly BACish today. On 5th Oct, 2014 Shauna said:
What that's crazy, you go commando hahaha! How heavy is your helmet ? The Morris Ital assassin! |
||||||
|
4018 Posts Member #: 1757 Back to Fucking Tool status Swindon |
30th Nov, 2013 at 02:28:44am
Can you get hold of a continuity tester or borrow one? It will allow you to narrow down the area at fault, just make sure no computers are connected as they don't like the test Drives
|
||||||
|
1713 Posts Member #: 8480 MS Paint flat cap champion & Morris Ital Lover From Sheffield now live in York tha noz |
30th Nov, 2013 at 07:23:03am
Paul-the test you refer to is an insulation resistance test used to prove any leakage faults live-earth or neutral-earth and would only be of use on the motors in this case.
Edited by oli79 on 30th Nov, 2013. On 18th Oct, 2013 apbellamy said:
I am feeling particularly BACish today. On 5th Oct, 2014 Shauna said:
What that's crazy, you go commando hahaha! How heavy is your helmet ? The Morris Ital assassin! |
||||||
|
Site Admin ![]() 9407 Posts Member #: 58 455bhp per ton 12 sec 1/4 mile road legal mini Sunny Bridgend, South Wales |
30th Nov, 2013 at 08:49:37am
Thanks for all the input guys, I'll grab a photo and upload today On 15th May, 2009 TurboDave said:
I think the welsh one has it right! 1st to provide running proof of turbo twinkie in a car and first to run a 1/4 in one!! Is your data backed up?? one extra month free for all Turbo minis members, PM me for detials |
||||||
![]() 6752 Posts Member #: 828 Post Whore uranus |
30th Nov, 2013 at 09:25:13am
one of my chaps on the flowbench forum wrote this jim ..
Medusa + injection = too much torque for the dyno ..https://youtu.be/qg5o0_tJxYM |
||||||
|
4018 Posts Member #: 1757 Back to Fucking Tool status Swindon |
30th Nov, 2013 at 10:33:13am
That is the test I ment, and I thought he was after finding the leakage? Which was causing the problem, it can be used on cpc and any other wires so long as its not sensitive, so start button, safety stops ect can still be checked not just the motor, it will prove if it is the cpc/earth causing the problem or if it is line or natural shorting as well.
On 30th Nov, 2013 oli79 said:
Paul-the test you refer to is an insulation resistance test used to prove any leakage faults live-earth or neutral-earth and would only be of use on the motors in this case. a continuity tester in the terms of domestic electrical use is used to measure the resistances of fixed wiring earth cables which in turn is used to determine the zs for each circuit, the importance if which I mentioned above. Either way its going to tell you fuck all, the motors are not connected directly to the mains supply- the drive/ inverter is, my issue is my real world knowledge of rotary phase converters is very limited but I have heard it disscussed before by others also in the trade that the dc feedback they provide can cause rcd issues Drives
|
||||||
|
1713 Posts Member #: 8480 MS Paint flat cap champion & Morris Ital Lover From Sheffield now live in York tha noz |
30th Nov, 2013 at 04:29:32pm
Paul- insulation resistance testers / meggers are for testing fixed wiring not machines/ appliances. In fact the only other thing I would dream of using it in would actually be the motor itself-nothing wrong with that, what you state about trying to locate the leakage is spot on, what I'm saying is these are not motors connected directly to the mains- there are vfm drives and a rotary phase converter in between On 18th Oct, 2013 apbellamy said:
I am feeling particularly BACish today. On 5th Oct, 2014 Shauna said:
What that's crazy, you go commando hahaha! How heavy is your helmet ? The Morris Ital assassin! |
||||||
|
1713 Posts Member #: 8480 MS Paint flat cap champion & Morris Ital Lover From Sheffield now live in York tha noz |
30th Nov, 2013 at 04:37:03pm
Roberts hit the nail on the head with a most probable cause and the solution,this is also what I have heard this from other sources during my time at work, all that concerns me is that Jims existing installation is capable of safely providing a non rcd protected supply, he is emailing me a pic, I will try my best to help. On 18th Oct, 2013 apbellamy said: